Delta can't or won't answer my question. Their dust collector motor is listed as 1 hp, 120v-12a. Does that mean 12 amps continously or only to start? That would make a big difference to me.
Electric motor question
Collapse
This topic is closed.
X
X
-
that's correct, the runnig current would be 12 Amps. Starting current is typically 4-10 times greater but for much less than a second and will not trip a circuit breaker that will normally handle 12 Amps.
Furthermore, it will only draw maximum running current of 12 Amps when the blower is unimpeded by flow restrictions such as long, small diameter pipe and plugged filter bags... any restrictions will reduce the current in more or less proportion to the flow rate.
Loring in Katy, TX USA
If your only tool is a hammer, you tend to treat all problems as if they were nails.
BT3 FAQ - https://www.sawdustzone.org/forum/di...sked-questionsComment
-
Any if you have any question about actual draw, you can get an ammeter at Radio Shack for something like $20.Comment