  • Russianwolf
    Veteran Member
    • Jan 2004
    • 3152
    • Martinsburg, WV, USA.
    • One of them there Toy saws

    #1

    220 to 110 volt change

    Okay, I freed up a 220v outlet by ridding my home of one of the baseboard heaters (replaced with a propane fireplace), so how can I make use of this in my shop? So far all my tools are wired for 110v.

    Do I simply run this to a location and take one of the hot wires to one outlet and the other to a second and the neutral to both?
    Mike
    Lakota's Dad

    If at first you don't succeed, deny you were trying in the first place.
  • gary
    Senior Member
    • May 2004
    • 893
    • Versailles, KY, USA.

    #2
    No, you could overload the Neutral. Why not use the breaker space to run a 60A subpanel to your shop?
    Gary

    Comment

    • Russianwolf
      Veteran Member
      • Jan 2004
      • 3152
      • Martinsburg, WV, USA.
      • One of them there Toy saws

      #3
      sounds complicated. what would I need to do?
      Mike
      Lakota's Dad

      If at first you don't succeed, deny you were trying in the first place.

      Comment

      • LCHIEN
        Super Moderator
        • Dec 2002
        • 21981
        • Katy, TX, USA.
        • BT3000 vintage 1999

        #4
        is the outlet close to your shop? Are you trying to use the wiring?
        If the outlet is elsewhere in the house and the wiring goes nowhere near your shop then all you really have gained is a breaker slot, but most breaker boxes will have spare slots, anyway. Maybe you gained some extra current availability, if you main breaker was heavily loaded...

        what do you need?
        Last edited by LCHIEN; 12-29-2007, 11:31 PM.
        Loring in Katy, TX USA
        If your only tool is a hammer, you tend to treat all problems as if they were nails.
        BT3 FAQ - https://www.sawdustzone.org/forum/di...sked-questions

        Comment

        • LinuxRandal
          Veteran Member
          • Feb 2005
          • 4890
          • Independence, MO, USA.
          • bt3100

          #5
          Anything ELSE on the outlet? Some 220 are required to be seperate, others are not. It WILL make a difference as to what can be put on that and to what extent.
          She couldn't tell the difference between the escape pod, and the bathroom. We had to go back for her.........................Twice.

          Comment

          • Russianwolf
            Veteran Member
            • Jan 2004
            • 3152
            • Martinsburg, WV, USA.
            • One of them there Toy saws

            #6
            the outlet is 6 inches above and 10 foot from my shop space. But the wire runs even closer.

            I'll have to check what else is on the circuit. Most likely another baseboard heater, but It will likely give me another reason to kill another heater, especially if it's in a little used room.

            What do I need? I would like another circuit in the basement/shop so that I will have less problems with running things at the same time. Or if nothing else more lighting.
            Mike
            Lakota's Dad

            If at first you don't succeed, deny you were trying in the first place.

            Comment

            • reddog552
              Established Member
              • Dec 2006
              • 245
              • Belleville Il.
              • Bt3000

              #7
              220 volt

              What wire size are we talking about. also what size breaker.
              The bitterness of poor quality lingers long after the sweetness of low cost is forgotten!

              Comment

              • Crash2510
                Senior Member
                • Feb 2006
                • 830
                • North Central Ohio

                #8
                overloading the neutral is typically not a problem with 220 because you are pulling current from both legs of your panel. Because the the neutral from both legs fluctuate on a different sine wave sharing a neutral is usually not a problem. The reason this is usually not done is becuase the hot wires could be hooked up to the same phase therefore call for the neutral at the same time. If you are sure that both hots are hooked up to seperate phases sharing the neutral will not be a huge problem.
                Phil In Ohio
                The basement woodworker

                Comment

                • Crash2510
                  Senior Member
                  • Feb 2006
                  • 830
                  • North Central Ohio

                  #9
                  sorry tried to find something to show you what i mean

                  from http://www.dotznize.com/electric/?a=sh

                  Q: Can two circuits share one neutral?
                  A: Yes, if it is done right.
                  Consider a three-conductor cable (red, black, and white) that originates at two circuit breakers which are connected to opposite poles, and the neutral buss bar. One can connect a 120-volt load between the red and white wires, placing that load on one of the circuit breakers, and one can connect another 120-volt load to the black and white wires to place it on the other circuit breaker. The breakers, of course, are sized appropriately to protect the wiring. But what about the current in the white wire? The white wire is the return for both loads. Won't it be carrying more than its rated current?

                  The answer is that the neutral does not carry the sum of the two currents; it carries the difference. If both loads draw the same amount of current, the neutral will carry no current. The voltage on one "hot" wire is always of opposite polarity to the voltage on the other "hot" wire. Therefore, the current returning by way of the white wire for each circuit flows in the opposite direction to the current for the other circuit, so that the two currents subtract, and the white wire can never carry more current than one of the two "hot" wires. This technique is called a multiwire circuit.

                  Beware, however, of connecting to the wrong breaker. If the two breakers supplying the two "hot" wires are connected to the same pole, the voltage on both hot wires will be of the same polarity, and the current for each of the two circuits will return in the same direction through the white wire, and thus add together. The white wire may carry as much as twice the rating of the circuit. This is a dangerous condition.

                  To check that a multiwire circuit is supplied correctly, measure the voltage between the two "hot" wires. If the two "hot" wires are connected to opposite poles, as they should be, there will be a difference of 240 volts between them. If they are incorrectly connected to the same pole, there will be zero (or nearly) volts between them.

                  There are some restrictions on the use of multiwire branch circuits, including these (2002 NEC 210.4):

                  "All conductors must originate from the same panelboard."
                  If a multiwire circuit in a "dwelling unit" supplies "split-wired" receptacles, a means must be provided to disconnect both ungrounded conductors simultaneously. This can be done with a two-pole switch, but usually it is done by tying the handles of the two circuit breakers together.
                  The same simultaneous disconnection requirement also exists if the circuit supplies a mixture of 120v and 240v loads (whether or not in a "dwelling unit"), but the disconnection means must be the "branch circuit overcurrent device" (the circuit breaker).
                  Phil In Ohio
                  The basement woodworker

                  Comment

                  • LinuxRandal
                    Veteran Member
                    • Feb 2005
                    • 4890
                    • Independence, MO, USA.
                    • bt3100

                    #10
                    Your going to have to look at your tools and usage. I have tried to make mine, so I could have one tool going, and start up something else (in the very rare event I ever had help).

                    For me, the 220, in a woodshop, would then be something that would need to run when anything else ran, like a dust collector, or maybe a compressor.
                    She couldn't tell the difference between the escape pod, and the bathroom. We had to go back for her.........................Twice.

                    Comment

                    • Russianwolf
                      Veteran Member
                      • Jan 2004
                      • 3152
                      • Martinsburg, WV, USA.
                      • One of them there Toy saws

                      #11
                      It's either a 15 or 20amp double circuit. (I have 1 15amp and 2 or 3 20 amp circuits for my heaters that take up two breaker spaces each, no clue why the two amperages).



                      But I also just noticed something else. I have a 30 amp double circuit and a 50 amp double circuit. The 30 if for "outdoor" so I'll have to figure out what exactly it is, likely the A/C. The 50 amp though is for the electric range. Well, we swapped out the electric range for a propane burner when we moved in........ So I have a free 50 amp 220 circuit also that is right above my shop.

                      Can I assume that since these are using 2 breaker spaces, that they are wired as Crash mentioned above?
                      Mike
                      Lakota's Dad

                      If at first you don't succeed, deny you were trying in the first place.

                      Comment

                      • reddog552
                        Established Member
                        • Dec 2006
                        • 245
                        • Belleville Il.
                        • Bt3000

                        #12
                        unused 50 amp ckt.

                        Ok now were getting somewere. I would take your unused Range 50 amp circuit and use it for a sub pannel for your shop. A 50 amp ckt. should be run with 6/3 w grd. you can install a small panel say 100 amp with 8 spaces for breakers. this will give you a lot of options.As for the unused 220 volt ckt I would take it back to a 110 volt ckt just swap out the breaker for a single pole breaker take the black wire to the breaker ground & white to the side bars.
                        The bitterness of poor quality lingers long after the sweetness of low cost is forgotten!

                        Comment

                        • Black wallnut
                          cycling to health
                          • Jan 2003
                          • 4715
                          • Ellensburg, Wa, USA.
                          • BT3k 1999

                          #13
                          Originally posted by Russianwolf
                          Can I assume that since these are using 2 breaker spaces, that they are wired as Crash mentioned above?
                          Yes, I think that is a good assumption but it would be best if you were to check it at the breaker as Crash detailed with a multimeter to confirm. FWIW I used split duplexes when I did my shop wiring. One with both my saw and shop vac (current DC) plugged into one outlet with two circuits leading to it and then six seperate outlets feeding my celing mounted flourescent lighting, each duplex split feeding seperate fixtures on seperate circuits.

                          So to answer your origional question you may split the wires to either two outlets or a single outlet, but I think you will need to keep the outlets in the same box and keep the disconnecting means tied together.
                          Donate to my Tour de Cure


                          marK in WA and Ryobi Fanatic Association State President ©

                          Head servant of the forum

                          ©

                          Comment

                          • reddog552
                            Established Member
                            • Dec 2006
                            • 245
                            • Belleville Il.
                            • Bt3000

                            #14
                            So to answer your origional question you may split the wires to either two outlets or a single outlet, but I think you will need to keep the outlets in the same box and keep the disconnecting means tied together. I have to dissagre with you here,SORRY. You need to replace the double pole with 2 single pole breakers of the same rating.This is the only both circuts will be protected.
                            The bitterness of poor quality lingers long after the sweetness of low cost is forgotten!

                            Comment

                            • Hellrazor
                              Veteran Member
                              • Dec 2003
                              • 2091
                              • Abyss, PA
                              • Ridgid R4512

                              #15
                              Don't split a 220 into 2 110 circuits. Either bump it up to the 50A, pull #6 wire and put in a subpanel or install 2 15A breakers in the place of the 15A 220.

                              Comment