    #16
    Originally posted by JBCrooks
    We very seldom work in Anderson, so I am not so familiar with their requirements. I don't think they require quite as much as in Pickens. I would just be leary about putting in seperate ground rods that aren't connected. We usually get one or two service calls a year where people do that and keep getting "shocked"
    Thanks JB. Coincidentally, a couple of Blue Ridge techs (not linemen) were out yesterday to put some monitoring equipment in the meter box to monitor incoming voltage. BR runs 245V+ and they have had some reports of this causing problems.
    I asked them about the grounding and neutral/grounds. They said when running from a main house subpanel via a breaker to a breaker panel in the detached building, that there should never be ground rods at both locations due to there possibly being a differential in the grounds, and that the ground and neutral in the panel in the detached building should be tied together.
    This gets more and more confusing.

    Comment

    • JimD
      Veteran Member
      • Feb 2003
      • 4187
      • Lexington, SC.

      #17
      Ken,

      Are you getting a permit? If you are, I would ask the inspector - that's what counts in the end (at least in terms of passing inspection).

      Jim

      Comment

      • Ken Massingale
        Veteran Member
        • Dec 2002
        • 3862
        • Liberty, SC, USA.
        • Ridgid TS3650

        #18
        Originally posted by JimD
        Ken,

        Are you getting a permit? If you are, I would ask the inspector - that's what counts in the end (at least in terms of passing inspection).

        Jim
        Jim,
        No, this started as a conversation on whether a friends existing wiring was done correctly/safely or not. now I don't know if mine is anymore.

        Comment

        • Hellrazor
          Veteran Member
          • Dec 2003
          • 2091
          • Abyss, PA
          • Ridgid R4512

          #19
          Originally posted by Ken Massingale
          They said when running from a main house subpanel via a breaker to a breaker panel in the detached building, that there should never be ground rods at both locations due to there possibly being a differential in the grounds, and that the ground and neutral in the panel in the detached building should be tied together.
          This gets more and more confusing.
          The ground rod always starts an arguement on which is the right way. You NEVER bond the ground and neutral in a subpanel.