Sounds like a plan Sarge. I don't think there would have been any danger in what you had in mind......separating the two sides and using one for the ground bar and one for the neutral bar. But it's a very good point that as you filled up the box you would fill up that neutral bar and not have the spots you needed.
The neutral bar needs to be floating inside that box and not bonded to anything else except the neutral from the main panel. The ground bar needs to be bonded to the box itself and to the ground from the main.
What you're going through is the only way I learn anything......you have to hear people say the same things over and over a little different way until it all makes sense to you. I never want to proceed with anything until I have that comfort level in my own mind that I know all the steps I have to go through to get the job done -- especially with something electrical like this. I probably make things a lot more complicated than they have to be but it's the only way the stuff sinks into my thick skull ! haha
Steve
The neutral bar needs to be floating inside that box and not bonded to anything else except the neutral from the main panel. The ground bar needs to be bonded to the box itself and to the ground from the main.
What you're going through is the only way I learn anything......you have to hear people say the same things over and over a little different way until it all makes sense to you. I never want to proceed with anything until I have that comfort level in my own mind that I know all the steps I have to go through to get the job done -- especially with something electrical like this. I probably make things a lot more complicated than they have to be but it's the only way the stuff sinks into my thick skull ! haha
Steve