Morning..
I had to add a sub-panel to be able to run a 2nd 220 v 30 A circuit. I came up short of space in the main panel box. By removing the existing 30 A 220v circuit breaker with intentions of moving it to the "sub" along with another 220v 20 A circuit, a space is left free for a 220v breaker in the main.
I intend to put a 60A 220 breaker in the main in that spot and run 6/3 wire to the sub panel. The question which is almost (almost is not for certain as I will be before connection) self explanatory is:
I do believe that 4 wires are required to go to the sub-panel. The two "hots" (black & red) go to the hot lugs. The ground wire to the ground lug and here's the question. I am assuming that the 4th wire must be bonded from the neutral bar in the main box to the neutral bar in the sub panel?
Even though I will be running 2 220v circuits from that sub box and a neutral wire is not required for them in that case, I assume the bond should be made from the neutral in the main panel to neutral in sub-panel with a neutral wire in case I want to add a 110v line that does require 1 hot.. a neutral and a ground connection from any panel period?
Am I correct or am I just assuming? Electrical guru's explanations are indeed Welcome!
Regards...
I had to add a sub-panel to be able to run a 2nd 220 v 30 A circuit. I came up short of space in the main panel box. By removing the existing 30 A 220v circuit breaker with intentions of moving it to the "sub" along with another 220v 20 A circuit, a space is left free for a 220v breaker in the main.
I intend to put a 60A 220 breaker in the main in that spot and run 6/3 wire to the sub panel. The question which is almost (almost is not for certain as I will be before connection) self explanatory is:
I do believe that 4 wires are required to go to the sub-panel. The two "hots" (black & red) go to the hot lugs. The ground wire to the ground lug and here's the question. I am assuming that the 4th wire must be bonded from the neutral bar in the main box to the neutral bar in the sub panel?
Even though I will be running 2 220v circuits from that sub box and a neutral wire is not required for them in that case, I assume the bond should be made from the neutral in the main panel to neutral in sub-panel with a neutral wire in case I want to add a 110v line that does require 1 hot.. a neutral and a ground connection from any panel period?
Am I correct or am I just assuming? Electrical guru's explanations are indeed Welcome!

Regards...
Comment