I understand that it is acceptable to place two circuits on one breaker (assuming the load is within limits) by pig-tailing as opposed to placing two cables under the breaker terminal. However, can the same thing (pig-tailing) be done with the neutrals or grounds, when the buss bar is full and a new circuit is being added?
Breaker Box Wiring
Collapse
This topic is closed.
X
X
-
I understand that it is acceptable to place two circuits on one breaker (assuming the load is within limits) by pig-tailing as opposed to placing two cables under the breaker terminal. However, can the same thing (pig-tailing) be done with the neutrals or grounds, when the buss bar is full and a new circuit is being added? -
I've seen pigtailing done in panels. My transfer switch is wired that way. It has to be. As long as it doesn't violate fill requirements it is ok but t can be messy. That said, if you can I would not put 2 wires under one breaker, I would put a junction box outside the sub panel and only have one wire running into the panel. Then there is only one wire connected to the breaker and you don't need to worry about filling up the neutral/ground busses.
edited to add... any splices I do unless they are temporary (not more than a week) are done with crimps rather than wire nuts. Much more secure and take up less room in the box.Last edited by crokett; 10-29-2008, 09:45 AM.David
The chief cause of failure in this life is giving up what you want most for what you want at the moment.Comment
-
If you have 1" wide breakers now you may be able to buy a double breaker to actually have two circuits per 1" breaker spot. To avoid pigtailing you could add an additional buss bar for yout nuetral/ ground which if this is your main panel should be bonded to the box. If it is a sub panel you will need seperate nuetral and ground with the nuetral not bonded but isolated to the box. HTH
This actually might be a good question to ask either your local inspector or a licensed electrician.Donate to my Tour de Cure
marK in WA and Ryobi Fanatic Association State President ©
Head servant of the forum
©Comment
-
Thanks for all your comments. My main question is not about the breaker (I have room for addl breakers), but about the buss bar, which is full. If I do pig-tail to attach to the buss bar, would I have to step up to a larger gauge for the pig-tail?SOW YOUR WILD OATS ON SATURDAY NIGHT - - - THEN ON SUNDAY PRAY FOR CROP FAILURE!Comment
-
technically i can't think of a reason you would (need to up the gauge), the amperage is the same as going through the one breaker if you are bringing the two circuits attached to the breaker back in to the neutral buss.Loring in Katy, TX USA
If your only tool is a hammer, you tend to treat all problems as if they were nails.
BT3 FAQ - https://www.sawdustzone.org/forum/di...sked-questionsComment
-
Lchien, I am talking about bringing the neutrals from two different breakers together at the buss bar. I do not have two leads on any of my breakers, as I have enough room for the number of breakers needed. I just mentioned pig-tailing the breakers as an illustration of an allowed similar practice. My concern is that since this represents tieing together two different circuits, am I not increasing the possible current flow at the point where I connect the neutrals?SOW YOUR WILD OATS ON SATURDAY NIGHT - - - THEN ON SUNDAY PRAY FOR CROP FAILURE!Comment
-
They sell additional bus bars that can be used for the grounds, at least for some brands of panels. I would look into that first. I also read somewhere (code experts could fill in the detials) that it is OK to put two grounds under a screw in a bus bar, but neutrals all need their own screw. But look for the ground bars first. They don't cost that much, and would probably be the best way to do it. I think that you just screw them to the panel, and that carries the ground.
JimComment
-
In other words, the answer appears to be, "It depends."LarryComment