A table saw motor in a hobbyist wood shop is not a continuous-duty motor. That would be for things like air conditioners, pumps, air compressors in auto repair shops, etc.
I think these provisions are generally applied to machinery that is hardwired, with a disconnect switch. The code has no way to regulate what lay people plug into a given circuit -- that's the whole point of breaker sizes, wire gauges, etc. If someones does something dumb, the breaker trips before the wire melts and starts a fire.
That said, I agree with the conclusion. My 3HP cabinet saw is on a 20A circuit with 10ga wire.
I think these provisions are generally applied to machinery that is hardwired, with a disconnect switch. The code has no way to regulate what lay people plug into a given circuit -- that's the whole point of breaker sizes, wire gauges, etc. If someones does something dumb, the breaker trips before the wire melts and starts a fire.
That said, I agree with the conclusion. My 3HP cabinet saw is on a 20A circuit with 10ga wire.