    Dehumidifier causing lights to dim

    Since the weather is starting to get warmer, we've had our humidifier running in our basment. I've noticed that when the compressor kicks on in will cause some lights to quickly dim, then return to normal in other rooms. I've check the pannel an everything is fine.

    I did some research online and came across an acticle that suggested it could be the fact that I have a 20 amp breaker below a 15 amp breaker. The 20 amp is for my basement and runs the dehumidifier as well as other tools. The article suggested that when the dehumidifier kicks on it will pull some current from whatever is on on top of the breaker. So, say a light is on in a bedroom and the dehumidifier kicks on, it would cause that light to dim. The solution, the article suggests, would be to move the 20 amp above any 15 amps in the pannel.

    Any problems with not doing this, ie, would it cause any longterm problems to the electrical system? Is this the problem/solution?
    -Justin


    shepardwoodworking.webs.com


    ...you can thank me later.
  • toolguy1000
    Veteran Member
    • Mar 2009
    • 1142
    • westchester cnty, ny

    #2
    as all breakers are fed equally through the buss bars, i don"t see how the location of anything in the main panel would matter. a load applied to a panel with inadequate service would cause other appliances (lights) to dim when that load is initially applied. i'll be watching this thread for a definitive response.
    there's a solution to every problem.......you just have to be willing to find it.

    Comment

    • All Thumbs
      Established Member
      • Oct 2009
      • 322
      • Penn Hills, PA
      • BT3K/Saw-Stop

      #3
      It may be an inrush current issue. Especially if the compressor is getting old (harder to start) or is cycling a lot.

      So even though it may be rated at 15 or 20 amps, it may be pulling multiples of that when the compressor kicks in. Here is an article that says inrush can be 7 to 8.5 time the normal operating current:

      http://www.inspectapedia.com/aircond/aircond06.htm

      Comment

      • Daryl
        Senior Member
        • May 2004
        • 831
        • .

        #4
        Your breaker box will have two main circuits in it, I think the article meant to switch that breaker over to the other circuit, the spot above it would be the other circuit. Your wiring should be pretty much balanced so there likely won't be much of a difference.
        If you are using an extension cord, use a heavier guage and or shorter one.
        You may be able to get a "hard start" kit, which is a large capacitor to even out the current draw on start up.
        Sometimes the old man passed out and left the am radio on so I got to hear the oldie songs and current event kind of things

        Comment

        • RAFlorida
          Veteran Member
          • Apr 2008
          • 1179
          • Green Swamp in Central Florida. Gator property!
          • Ryobi BT3000

          #5
          Justin, all that's been posted is correct.

          Your motor pulls high current to start (as already stated). By placing the breaker in questions to the other hot leg in the panel not associated with the lights you speak of, may cause lights that are on THAT leg to dim. It's more than likely high current draw. If you have a clamp-on amp meter, you could tell a little about it.