    #1

    Electrical Wiring Question

    What is the (minimum) gauge wire for running a 50 amp sub panel? Am I not allowed to have a separate ground for the sub, or do I have to pull a fourth wire?

    Im sure it vary from region to region but I am also sure that there is a general answer to this question!

    Raffi
  • LJR
    Established Member
    • Jan 2005
    • 136
    • .

    #2
    Minimum size wire for a 50 amp load would be #8 wire.

    Grounding is a whole separate chapter by itself in the NEC so it's hard to make a general statement. The main panel and it's subpanels must be on the same ground plane, in short that means you have to pull a ground wire from the main to the subpanel. You can add more grounding capacity to the system at the subpanel by connecting to a driven ground rod or another approved ground but that doesn't allow you to do without the ground wire to the main panel.

    Comment

    • scorrpio
      Veteran Member
      • Dec 2005
      • 1566
      • Wayne, NJ, USA.

      #3
      For a 50 amp sub, I'd use an 8/3 wire plus ground. And make sure neutral and ground is not connected on the sub. Neutral and ground should connect only at one spot: the main panel. And most codes prohibit using conduit or cable BX jacket as ground.

      Comment

      • Hellrazor
        Veteran Member
        • Dec 2003
        • 2091
        • Abyss, PA
        • Ridgid R4512

        #4
        What is the sub for? answers are different depending if its within the house or to a garage, workshop, etc.

        Comment

        • Raffi
          Established Member
          • Sep 2003
          • 198
          • CA, USA.

          #5
          Wow thanks for the well thought out replies. The sub is going in my (detached ) garage. It will feed my saw and other tools, maybe a window air conditioner.

          Some years ago I began planning upgrading our main service panel, and running a sub to the un serviced garage. I ran a 3/4 pipe to the garage from near where the new panel will go. My electrician friend says I need to have a 1" pipe cause he feels that 6 gauge is required.

          Thats basically it. I want to avoid having to re trench to put in 1" pipe lol.

          Raffi

          Comment

          • Hellrazor
            Veteran Member
            • Dec 2003
            • 2091
            • Abyss, PA
            • Ridgid R4512

            #6
            Ok since its a detached structure, whats the total distance from the panel in the house to the planned location of the panel in the garage? Include the height changes (conduit depth up to the panel height). The wire size required will depend on the distance of the run and voltage drop issues.

            You also need to run a ground to the garage and install a ground rod at the garage.

            Comment

            • Raffi
              Established Member
              • Sep 2003
              • 198
              • CA, USA.

              #7
              Mike thanks for taking the time to reply. I'd guess nearly 60' from the main to the new sub.

              Comment

              • Hellrazor
                Veteran Member
                • Dec 2003
                • 2091
                • Abyss, PA
                • Ridgid R4512

                #8
                Ok, you shouldn't have to worry all that much about voltage drop. 100' is where you should bump up to 1 size larger wire.

                Comment

                • Raffi
                  Established Member
                  • Sep 2003
                  • 198
                  • CA, USA.

                  #9
                  Your the man Mike.

                  Thanks a ton.

                  Raffi